ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 524 guests, and 23 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#39739 06/28/04 10:31 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline OP
Member
I have seen 800 amp services using two 500 kcmil conductors for each phase. I'm assuming that the ampacity is figured as 430 amps(THHN) X 2 = 860 amps, rather than as being equivalent to one 1000 kcmil conductor at 615 amps. Would three 250 kcmil parallel conductors be 290 amps X 3 = 870 amps?

Dave

#39740 06/28/04 10:53 PM
Joined: Aug 2001
Posts: 599
N
Member
The ampacity is figured using the 75 deg table (380A). Times two conductors is 760A. Then article 240.4 is applied allowing the next higher standard fuse size or 800A.

#39741 06/29/04 09:33 AM
Joined: Dec 2003
Posts: 751
E
Member
The 75 degree section is used because of the rating of the termination lugs. See 110.14(C).

Remember also to apply 310.15(B)(2)(a) and derate the conductors if you pull all of the paralled conductors in one conduit.

Earl


Earl
#39742 06/29/04 12:04 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The 75C column must be used because UL does not list Overcurrent Protective Devices for use with conductors based on 90C ampacities.

#39743 06/29/04 05:24 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
One little detail to watch out for is to be sure that the noncontinuous load plus 125% of the continuous load does not exceed 760 amps for parallel 500kcmil. This is usually not the case since most of us don't cut these things real close to the bone & leave some room for future growth.

Tom


Few things are harder to put up with than the annoyance of a good example.

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5