#39496 06/22/04 01:03 AM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Hello all.
Can i have a SO hard usage cord be droped from a 20foot ceiling with double duplex receptacles to be used as permenant power source for commercial washing machine?

Where is SO cord used as freely hanging from a ceiling? Ofcourse with proper cable grips.

Thank you
Edward


Thanks
Edward
Joined: Jan 2003
Posts: 46
B
Member
I would say no. See 400-8 1999NEC

Joined: Oct 2000
Posts: 2,749
Member
314.23(H) Pendant Boxes.

An enclosure supported by a pendant shall comply with 314.23(H)(1) or (2).

(1) Flexible Cord. A box shall be supported from a multiconductor cord or cable in an approved manner that protects the conductors against strain, such as a strain-relief connector threaded into a box with a hub.


Joe Tedesco, NEC Consultant
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
here is what am planning to do:
A 10-3 SO cord suspended from 20 foot ceiling and be used as a permenat installation.(with proper cord grips and strain relief connectors)

Am I in violation of NEC. I know i can not have the cord attached to the surface of the building.BUt i am suspending it from the ceiling.
Another option i have is to run unistrut from ground up and have a counduit straped to the unistrut.

Thank You
Edward


Thanks
Edward
Joined: Apr 2002
Posts: 2,527
B
Moderator
It took advance negotiation with the AHJ, but I have used Appleton STB***SR- or STN***SR-series “basket-grip” liquidtight flexible-metal conduit connectors for (temporary/one-year) vertical-only spans where the bottom ends were non-anchored floor-elevation equipment.

Page 7-8 www.appletonelec.com/pdf/ST-2thru13.pdf [Hubbell and T&B also make ‘em.]

Here’s one consideration for article-400 wiring—in the case of flexible cord for “drop” duty, it is well worth avoiding the pervasive “commodity-grade” type-S** neoprene- or vinyl-jacketed cord. A lot of that stuff has embarrassingly {and litigiously} poor durability—used inside or out.




[This message has been edited by Bjarney (edited 06-22-2004).]

Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Edward:
Flexible cord code compliant uses, and NON-compliant uses are stated in NEC 400.7 (Uses Permitted) and 400.8 (Uses Not Permitted).

Basically, there is not a whole lot that 'cord' can be used for any more. I, and many others have used 'cord' drops as you mentioned, but around '99 the AHJ's started basically what we call "no mo' cord"

And BJ, no we (I) used the 'good stuff', not the economy throw away butched extension cords.

John


John
Joined: Sep 2003
Posts: 650
W
Member
400.7(A)(1) specifically permits 'pendants'.

There is no definition of 'pendant' in article 100, but 210.50(A) states 'A cord connector that is supplied by a permanently connected cord pendant shall be considered a receptacle outlet'

IMHO a 'pendant' receptacle is recognized and permitted by code.