Any code problems with putting an 125A sub panel in a garage? If so, could somebody site the section please?
Not a problem at all. If the garage is a detached building, it needs its own grounding system.
If its an attached garage don't put it in the firewall.
Curt Swartz
If it is a detached garage it needs its own main breaker/disconnect 225.30 (Some AHJ's require this be on the exterior), and a EGC going back to the main house panel in addition to the grounding system at the garage. 250.32(A)
Mark Stetson
Mark Stetson Stetson Electric
Thanks for the rapid replies. The garage is attached, and my proposed location for the sub is on the wall between the garage and the interior of the house. Is this going to be a problem?
Thanks again!
Check for the fire wall rating, some local codes will require a 1, or 2 hour rating for a wall from a garage to dwelling space. Condo's especially! So in this case your openings would need to be of a certain (small TBA) size. Depanding on the fire code. Or you'll have to go with a surface panel. In some cases like this I'll have the general put up the rock where the panel will be, put a 14x14x4 box above it, stub all the cable evenly in a pattern into the back of it. (2 for larger circuit counts) Then a 2 1/2" nipple into the panel. This way, it's a pattern of small holes, (that you can feed and chalk from the back) as opposed to a 14x36" hole. Theres nothing sillier than a rock box, and chaulk for a panel!
I put cans in cieling that i didn't know was going to be fire rated once, boy was that a mistake!
Techgod, a separate EGC is not needed from the house to a detached garage as long as there are no other metallic connections between the two buildings (TV, phone, water pipe, etc...). However, I personally would never run only three wire for a detached garage (I doubt that any licensed/informed electrician would).
Shinnston, WV USA