Hi I'm a new Contractor (just over a year) and I'm doing a Church with a 600A service with 4 25kW electric furnaces. What would be the best (and most economical) way to do this service? any ideas?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
From 600 amp metering out to three 200 amp main breaker panels. I think that would be the least money in equipment. It also provides 126 poles right from the start. Just my guess. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2003
Posts: 36
OP
Member
|
How can you put 4- 107 amp furnaces in those panels. Correct me if I'm Wrong but you wouldn't put more than 1 per 200a panel. Also they might even upgrade to 30kW(128A) furnaces.
|
|
|
|
Joined: Jan 2003
Posts: 73
Member
|
DYNAMITE
This is assuming the feeders are 120/240 1 phase 3 wire?
Without knowing if there is any space limitations, your best option would probably be:
600 Amp Main fused Disconnect > 600 amp splitter install 4 x 200 amp fused disconnects off above splitter, wired from splitter to load side @ 200 amp and fuse for smaller units. (if upgrade on furnaces happen then it's only a fuse change Then come off splitter distribution panel (you can use the tap rule to keep panel size down, so it dose not need to be 600 amp. i.e. depending on load and circuits required maybe a panel with 400 or 225 amp mains will be good)
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
DYNAMITE. I assumed 3 phase - 480, sorry.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
CDN_ELECTRICIAN
Why would you need the 600 Amp Main fused Disconnect?
If the power company wants / allows hot sequence metering the main is not needed.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
The biggest influence is probably the serving utility’s metering compartment and underground pull-section dimensions. Guessing 208V 3ø, with four 90-amp furnace branch circuits. Each furnace: (25,000W/208V/1.732)*1.25 = 87 amperes… Rough guess 600A 300V class-T fused main and a 225A-bus panel/feeder for everything else.
|
|
|
|
Joined: Dec 2003
Posts: 36
OP
Member
|
240V single phase service in Canada.It's to bad I can't run 4 200A combimation panels straight from the CSTE, I really didn't want to use Switches for each furnace
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
If I was designing this job I would use a free standing switchboard which contained a pull section, CT compartment and distribution section. The distribution section could contain the 4 breakers for the heaters and 1 or 2 breakers supplying the panels for other loads. If less then 6 breakers are installed a main disconnect would not be needed. This would also make the grounding electrode/bonding very easy since you would just need to connect 1 panel.
From reading these forums over the past couple of years I see where things like this get done very differently around the country and Canada. Apparently it is cost effective to build a service like this in some areas but I couldn’t even purchase the materials for the cost of having a switchboard built. The only way I would every build something like is if I didn’t have time to wait for the gear to be build. I can usually get something like this in 3-4 weeks (sooner for more $$$) but seldom is the equipment needed for a new building that quickly.
Curt
Curt Swartz
|
|
|
|
Joined: Sep 2003
Posts: 650
Member
|
Dumb question: How would the costs change if you split the service, with a higher voltage service drop for the heaters and a 120/240V drop for your general lighting load? Is 575V available at the location; this would take the currents way down into the manageable range Separate question, and probably not the domain of the sparky involved; why 100KW of electric heat??? We are probably talking $10K-$30K USD for the electric bill to run these heaters, unless they are run very infrequently. I would think that something fuel burning, or a heat pump system, would be more cost effective over time; though I've never thought in terms of heating large buildings. -Jon
|
|
|