ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 384 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#38266 05/19/04 05:16 PM
Joined: Aug 2002
Posts: 141
E
elecbob Offline OP
Member
I'm wiring a pub and they want me to install CAT 5 cables for POS (Point of service) terminals. Does the code require me to install them in conduit since this is a large (12,000 sq. ft) commercial building?
bob

#38267 05/19/04 06:03 PM
Joined: May 2004
Posts: 8
P
Junior Member
Quote
Does the code require me to install them in conduit

NO, however you may be required to sleeve the cable, with EMT, throught any fire walls.


Also see 800.52(A)(2), Seperation from other conductors; 800.52(C), Equipment in other space used for environmental air; and 800.52(E), Support of conductors.

#38268 05/19/04 09:15 PM
Joined: Aug 2002
Posts: 141
E
elecbob Offline OP
Member
Thank you very nuh Mr. ProCircuit. That is exactly what I needed to know.
bob

#38269 05/20/04 05:02 PM
Joined: Jan 2003
Posts: 73
C
Member
Ran into this one regarding "OPEN Cables"

The Electrical Code: No Problem, unless a special classified area such as Explosion Proof and like ProCircuit stated Fire Seperations...
However, the building code (local building Inspector) caught us with Flame Spread of cables, he wanted FT6 rated cables installed or in conduit, as where the cables were run was classified as a "Return Air Plenum for the HVAC (we were running in "T-bar Ceiling).


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5