by ale348 - 03/29/24 01:09 AM
by NORCAL - 03/19/24 05:11 PM
#34786 02/23/04 03:56 PM
SJT Offline OP
Is anyone familiar with the testing method to check that 25 ohms or less are at the ground rods. Here on L.I., we have a single ground rod as a supplement to the main water pipe. Has anyone used a clamp on style meter to check grounds? Are the 3,4 type terminal testers better?
Thanks
#34787 02/23/04 05:02 PM
I have used the clamp on with pretty good success. You have to clamp on at the last ground to the ground rod. The meter I use is made by AMEC and it will read 0.7 ohms if you have not connected on the last lead. The 3, 4 terminal testers are good but if you are just seeing if you are below 25 ohms, the clamp on is easier.
Jim
#34788 02/23/04 10:57 PM
#34789 02/25/04 04:03 PM
SJT Offline OP
Thank you for the pages on the Ground Test. It's an area that I would like to be more educated about. I appreciate both inputs.
