by Hutch - 05/13/24 04:23 PM
Electricians revenge
#34588 02/16/04 06:03 PM
jbfan Offline OP
Do I need to bond the neutral of a 208v to 120v control transformer. The panel that feeds the transformer has the ground and neutral bonded inside the panel. It is a 500va transformer.
Thanks
"Yes I am a Pirate, 200 years to late" Jimmy Buffett
#34589 02/16/04 06:30 PM
No, You can bond it or let it float at your option. I prefer to bond it...it makes voltage reading to ground more meaningful, makes troubleshooting easier.
GJ
[This message has been edited by golf junkie (edited 02-16-2004).]
#34590 02/16/04 07:53 PM
Please consider grounding the 120V-secondary winding. For 1000VA-and-under control-power transformers, NEC 250-30 allows the winding to be grounded with a simple 'case' jumper. The usual full-tilt grounding-electrode/building-steel connection is not needed. This is a real easy way to keep electrostatically-induced garbage off the control circuit.
[This message has been edited by Bjarney (edited 02-16-2004).]
#34591 02/16/04 08:53 PM
jbfan Offline OP
Thanks for the answers. It will be bonded tomorrow!
#34592 02/16/04 10:19 PM
I second Bjarney's suggestion!
Scott35