ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#34522 02/14/04 02:24 PM
Joined: Apr 2001
Posts: 507
G
Member
Does anyone have a chart for rule of thumb amperage draws on HVAC and refrigeration compressor based on tonnage??

For instance how many amps does a 208v, 3ph, 5 ton compressor draw?

GJ

#34523 02/14/04 03:05 PM
Joined: Jan 2004
Posts: 615
J
Member
Obviously you are looking for a way to estimate site unseen for ball-parking a bid or having some idea for sizing something. Just thought I'd say that before you get "You really should size it off the nameplate rating".

I don't know off hand for your example, but I've found for single phase 240 volt, about 10 amps per ton. That's breaker size. 5 ton 50 amp breaker, etc.

#34524 02/14/04 04:02 PM
Joined: Apr 2001
Posts: 507
G
Member
Jps,
You are correct, I'm looking for a ballpark estimate. The final circuit sizing will be done from the nameplate info.

We are running to more and more requests where people are trying to save on the engineering. Tough to bid when it's all rather undefined.

I found a conversion that says 1 ton=4.71HP. Going back to my example then I calculate;

5 ton = 5 x 4.71 = 23.55hp

The amp draw for that doesn't come close to matching carrier's data for a 5 ton RTU. Carrier says that a 5 ton RTU 208v, 3ph, has a FLA of 32A.

????????????????

#34525 02/14/04 05:57 PM
Joined: Oct 2001
Posts: 135
W
Member
12,000 BTU (1 ton) = 4.7161 horsepower hour as a raw calcultion with formulas.

It does not translate into hp/ton on small equipment.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5