255
16
I would like to use CAT 5 cable for lowvoltage (24) volt control wiring. I am planning to control 3Amp contact rating relays to operate window shutters. And am planning on using small N/O switches to control the relays.
Is the rating of the CAT 5 cable higher than 24 Volts?
Any other suggestions?
Edward
Thanks Edward
Posts: 1,498 Likes: 1
Check the cable. I had a look at some of the patchcords in the office: 300V (sic!)
The other rating I commonly find on computer cables is 30V. I think it would be technically impossible to manufacture a cable that could not handle this.
CAT5 as well as any of the other CAT cables are CL2 listed and as such are 150V. You will be fine.
Just as a suggestion... try using 18 gauge control wire. phone wire is only about 22 gauge.
I second Brian's suggestion for 18awg. Volt drop becomes an issue very quickly when you are starting with low voltage.
GJ
That was my first thought also but after rereading the question I think I understood that the 24ga wire will operate the coils of the relays through the switches. Not much current there so voltage drop shouldn't be a problem. The 3A current rating is for the relay contacts, not the current through the control wire.
Thanks for the reply.
The contact rating is 3 amps.
The voltage problem should not be a problem. I just need to verify that using a CAT 5 cable is an acceptable method in this application which sounds like it is. And i am not violating NEC.
Edward
Thanks Edward
Last time I checked 5 mins ago cat 5E is 26 Guage Might want to get 20 or 18 Guage wire
Theres always enough room in the junction box.You just need a bigger hammer
It is 24AWG. I think i will use thermostat wire 18AWG.
Edward
Thanks Edward
The stuff I have is 26 AWG it came with my cable modem. but the newer stuff is 24 Guage
Shinnston, WV USA
