by NORCAL - 03/19/24 05:11 PM
0 members (), 260 guests, and 19 robots.
#33663 01/27/04 10:55 AM
Edward Offline OP
I would like to use CAT 5 cable for lowvoltage (24) volt control wiring.
I am planning to control 3Amp contact rating relays to operate window shutters. And am planning on using small N/O switches to control the relays.
Is the rating of the CAT 5 cable higher than 24 Volts?
Any other suggestions?
Edward
Thanks
Edward
#33664 01/27/04 12:44 PM
C-H Offline
Check the cable. I had a look at some of the patchcords in the office: 300V (sic!)
The other rating I commonly find on computer cables is 30V. I think it would be technically impossible to manufacture a cable that could not handle this.
#33665 01/27/04 06:47 PM
CAT5 as well as any of the other CAT cables are CL2 listed and as such are 150V. You will be fine.
#33666 01/27/04 10:18 PM
Just as a suggestion...
try using 18 gauge control wire.
phone wire is only about 22 gauge.
#33667 01/27/04 10:42 PM
I second Brian's suggestion for 18awg. Volt drop becomes an issue very quickly when you are starting with low voltage.
GJ
#33668 01/28/04 01:15 AM
That was my first thought also but after rereading the question I think I understood that the 24ga wire will operate the coils of the relays through the switches. Not much current there so voltage drop shouldn't be a problem. The 3A current rating is for the relay contacts, not the current through the control wire.
#33669 01/28/04 02:46 AM
Edward Offline OP
Thanks for the reply.
The contact rating is 3 amps.
The voltage problem should not be a problem. I just need to verify that using a CAT 5 cable is an acceptable method in this application which sounds like it is. And i am not violating NEC.
Edward
Thanks
Edward
#33670 01/29/04 12:18 AM
Last time I checked 5 mins ago cat 5E is 26 Guage Might want to get 20 or 18 Guage wire
Theres always enough room in the junction box.You just need a bigger hammer
#33671 01/29/04 12:32 AM
Edward Offline OP
It is 24AWG. I think i will use thermostat wire 18AWG.
Edward
Thanks
Edward
#33672 01/29/04 12:52 AM
The stuff I have is 26 AWG it came with my cable modem. but the newer stuff is 24 Guage