1 members (Scott35), 534 guests, and 34 robots.
#33469 01/21/04 09:56 AM
According to what I understand in the code, an outside hot tub must be the same wiring methods as a swimming pool in regards to being wired in "rigid metal conduit, intermediate conduit, or nonmetallic rigid conduit etc... Am I correct in this interpertation??? Thanks Steve....
#33470 01/21/04 05:58 PM
That's correct except for 680.42(A)(1) that permits the use of liquidtight flex in lengths not longer than 6ft. for packaged or self-contained spas or hot tubs.
#33471 01/21/04 10:24 PM
I thought that any Chapter 3 method like NM-B could be used for the interior portion of the circuit until it hits the disco. Then it would need to switch methods and have an insulated ground wire.
#33472 01/21/04 10:33 PM
NM can be used for the interior portion provided the ECG is not smaller than No. 12 per 680.42(C)