0 members (),
228
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2003
Posts: 524
OP
Member
|
..Can anyone please give me the article # in "The Book", that addresses what colors the different phases are to be marked..I know that for 120/240v.3phase, the colors are black,red,and blue,and white for the neutral,...and for 277/480v. 3phase,it's yellow, orange,and brown..but is the neutral white, or gray??? and where does it have these color codings listed,I looked all over Art.200,...maybe I missed it..???
.."if it ain't fixed,don't break it...call a Licensed Electrician"
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
AR The NEC does not specify the colors for 480/277 or 208/120 "hots". If what you are replacing had colors for the sake of keeping things easy to work on I would keep them the same. White or gray are both acceptable for the Neutrals. Bob Hey be careful with the marking and installation of parallel cables. Before energizing this job put a continuity meter on it and check for cross phased or grounded conductors. Big Boom from cross phased parallel cables on service entrance conductors.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2003
Posts: 524
OP
Member
|
.."if it ain't fixed,don't break it...call a Licensed Electrician"
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
when the utilty inspector came by, he saw that the old lines were marked ..Red,Black,and Blue,and he said I had to change it cuz those colors denote a 120/240v.system,and the system was really 265/460.. Interesting, it could be a local amendment, a utility requirement or the inspector could just be out of his head.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
See 210.4(D) Identification of Ungrounded Conductors.
Where more than one nominal voltage system exists in a building, each ungrounded conductor of a "multiwire branch circuit," where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Joe service conductors are not a multiwire branch circuit and the colors are not specified.
How is that article you posted relevant to this installation?
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Bob:
If my message came second, there would have been no question in your mind.
The first question didn't mention that they were service entrance conductors!
I only posted it because I wanted to add some information!
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Nov 2003
Posts: 269
Member
|
There is an interesting thread on this subject on Mike Holt,s forum. Go here
John
|
|
|
|
Joined: Jul 2002
Posts: 241
Member
|
It looks like, if you have a situation where you have multi conductors of different voltages in the same raceway, wireway, etc., the nuetral would have to be marked white along with a marking on it to show it's from that system. I never had a situation where I had to do this, but to identify the nuetral on the 480v system, I wonder if white tape along with small wraps of brown, orange, and yellow also on the nuetral conductor would satisfy 200.6D. This would need to be done only if the nuetrals are mixed for whatever reason. Normally we keep boxes, wireways, separate. Happy New Year
|
|
|
|
Joined: Oct 2001
Posts: 597
Member
|
I'll second Bob's comment. Ask the utility inspector for the document that prescribes the color scheme, explaining that you'll need it again for future jobs, and explaining that the NEC doesn't spec the color. My local PoCo has had a tendancy to loose my mailing information, thus leaving me the task of finding out what I missed, generally after I've built something. Edit for sp. [This message has been edited by ElectricAL (edited 01-02-2004).]
Al Hildenbrand
|
|
|
Posts: 32
Joined: June 2004
|
|
|
|