Edward Offline OP
I have a client who has two shirt printing machines. One 240V@22Amps and other 240V@30Amps. Can I treat this installation like a dwelling cooking unit branch circuit calculation?
Pull a 50A feeder and use #8 or #10 taps for two different 30A plugs.
PS. machines are heating units to dry the ink on the shirts.And this is in a residential garage.
Please give code sections.
Thanks
Edward
Thanks
Edward
It seems that 210.21(B)(3)would prohibit this.
BTW,
Are the loads continuous and/or simultaneous?
[This message has been edited by Redsy (edited 12-23-2003).]
I would worry about zoning. Not too many towns allow businesses like this in a garage, and if they do, now you have a different occupancy to worry about. In a non-separated mixed occupancy there may be issues with the fire rating for the building. The BO or FM may require fire rated sheetrock and/or sprinklers to keep the garage business from burning up the house.
Electrically, I would have to re-compute the loads on the service. Do you need to upgrade the service for all this additional equipment?
Earl
Edward Offline OP
Redy,
Loads may be continuous and on at the same time.
Earlydean,
I do not need to upgrade the main panel. I was going to use a 50A braker from the subpanel.
Thanks
Edward
See Article 422.10(A) as well as 422.11 (D) &(E).
