|
1 members (Scott35),
216
guests, and
11
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2003
Posts: 172
OP
Member
|
Other than covering conduit in drywall is there any way or cables to give you two hour fire protection besides m.i.c.c.
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
Didn't even know conduit had a fire rating. What is the application?
If it's for something like a fuel farm (pumping station) you probably could not do better than MI, all in all, it does not come out a lot more than Rigid if you're running a bunch of it.
Walls are fire rated, the individual components inside them are dependent upon them to provide the rating. Many applications you do want to insure a low smoke in case of fire.
|
|
|
|
Joined: Aug 2001
Posts: 16
Member
|
If it's for Fire Pump or Emg. Cicuits VitaLink makes a 2 hr. mc cable. Check www.vitalinkcable.com
|
|
|
|
Joined: Oct 2003
Posts: 172
OP
Member
|
ITS FOR A COMMERCIAL FIRE ALARM INSTALLATION
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
I'm still confused. Why would a supervised Fire Alarm system need a two hour rating? In the case of a fire, the system (hopefully) would have performed it's function in the vicinity of the fire, and any damage to the system wiring would be a moot point. Roger
|
|
|
|
Joined: Oct 2003
Posts: 172
OP
Member
|
its spec,d this way for the risers
|
|
|
|
Joined: Aug 2003
Posts: 173
Member
|
That is the only place I have ever seen MI cable installed. Feeding a disconnect for a huge fire alarm panel in a shopping mall we used to service. It also fed the 480v., 100HP motor for the booster pump for the system. Before that I never even knew what the stuff was. Why not just use the MI?
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
|
|
|
|
Joined: Oct 2003
Posts: 172
OP
Member
|
The reason i don,t want to use m.i.is cost,if i can achieve the same result at less cost why not.
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
You can't buy MI cable in a fire alarm rated configuration.
Ron
|
|
|
Posts: 356
Joined: August 2006
|
|
|
|
|