#30845 10/29/03 11:43 PM
Whitey Offline OP
Maybe someone has run across this before,i was called to check some plugs in a school recently,the complaint was a fried microwave oven and computers,i tested the voltage at the plugs and it was 180V between neutral and the hot wire,also 117V between neutral and ground.There were 8 wires leaving the panel in emt feeding aprox 20 plugs,6 hots 2 neutrals,service to school is 3phase 4wire.It appears only one of the circuits was affected,a red circuit,i turned the breaker off one at a time until problem cleared,it appears a black circuit was causing the problem and the voltage returned to normal on the affected circuit.Is this a possible open neutral problem? any responses are appreciated.
#30846 10/30/03 06:01 AM
Sounds like maybe you have a 4 wire Delta system here!?
180-208 VAC from L-C would be found on one ungrounded conductor (typically ØB).
If not, look for open noodle situation on that branch circuit, or possibly on the Subfeed.
Scott35
#30847 10/30/03 09:41 PM
A problem with the panel or transformer bonding the nutral to ground?
#30848 10/31/03 11:10 AM
Whitey Offline OP
Just an update,turns out the problem was a neutral splice in a device box that was not twisted in the wirenut properly, intermittently under a heavy load, i believe it would arc and open circuit.
