ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 216 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#28806 08/31/03 02:33 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
I wanted to clarify my understanding of single phase on a three phase system:

single phase:

120v = one pole breaker
240v = two pole breaker

three phase:

120v or 277v single phase = one pole breaker
208v or 480v single phase = 2 pole breaker
208v or 480v three phase = 3 pole breaker


208v or 480v

#28807 08/31/03 02:46 PM
Joined: Aug 2001
Posts: 7,520
P
Member
You can have a single-phase circuit tapped from a three-phase supply either by connected phase-to-phase, or phase-to-neutral.

The breaker needs to open all ungrounded conductors, so with a 3-ph wye system a phase-to-phase load needs a 2-pole C/B, while a phase-to-neutral load needs only a single-pole, as you've stated.

The only cases that might want adding to your list would be something like a corner-grounded 240V delta, where one of the phases is actually grounded.

#28808 08/31/03 02:54 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
thanks paul. this forum is always a good place to turn to when your not sure. Thanks again.