ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#27886 08/08/03 12:07 AM
Joined: Mar 2003
Posts: 5
C
Carnak Offline OP
Junior Member
Update

The 416V transformers feed GE panel boards rated for 480/277. The single pole breakers are rated for 277V.

My concern here was I have never seen an air conditioning unit fed with a 240 hot and a neutral. The PTACs are all by GE so I have a call in to them.

A majority of the PTACs have been in service since 1989,so I am really wondering if I have been worried about nothing.


Go Big or Stay Home
#27887 08/08/03 05:51 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Wouldn't most American 240V A/C units (at least those intended for commercial use) be listed for more than 150V to ground?

They would need to be so rated for operation on a 240V corner-grounded delta supply, or if one side were connected to the high leg (208V) of a 4-wire delta.

#27888 08/08/03 06:32 AM
Joined: Mar 2001
Posts: 2,056
R
Member
BTW,
What does PTAC mean?

#27889 08/09/03 07:05 PM
Joined: Mar 2003
Posts: 5
C
Carnak Offline OP
Junior Member
PTAC- something to the effect of "Packaged Terminal Air Conditioner", the through-the-wall units you see in a lot of motels.

I think my concern boils down to does a motor 'care' how it is getting its power as long as the voltage, phase and frequency are correct.

It looks like the answer is no, the motor does not care.

I asked the manufacturer's engineer, and he spent a couple hours going through the NEC and could find nothing wrong.

The 150 to ground issue is not a problem with 3 phase equipment in a building powered by 240 open delta.


Go Big or Stay Home