In a 200A OH service tri-plex will be 1/0, should the riser also have 1/0, or 3/0 because it is in conduit? Riser will be CU THWN-2, Sun Resist.

[This message has been edited by Mike_Riverside (edited 07-06-2003).]

#27259 07/07/03 03:11 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Mike,

If this is a service for a dwelling, 2/0 copper is fine, if it is for any other occupancy, you'll need at least 3/0 copper.

Tom


Few things are harder to put up with than the annoyance of a good example.