Safety at heights?
0 members (), 228 guests, and 10 robots.
#270 01/05/01 06:51 PM
Can anyone tell me what the inrush current of a 480/208 75kva transformer would be if it was typically loaded on the secondary side at around 135 amps? I know it goes way high, but I need a ball park figure for argument sake. My boss wants to know why they keep popping the breaker when the transfer switch goes back to normal power. I need a ball park figure
#271 01/06/01 11:09 PM
Alan: I calculated the maximum inrush current for a 75 KVA transformer as 990 amps.
I do not know the duration. The secondary load is irrelevant for inrush calculations.
A circuit breaker with a time trip curve that will permit 990 amps, with a duration necessary to establish core flux, would be required for starting the transformer.