1 members (Scott35), 419 guests, and 10 robots.
#26615 06/16/03 09:16 PM
What is the purpose of two grounding rods? And, what is the code for distance between the two?
#26616 06/16/03 10:06 PM
Used for the code section about less than 25 ohms on ground rods or install 2 rod. the distance is not less than 6' apart Reference is 250.56 or .58 in 99 NEC, sorryI'm not under 2002 NEC yet.
#26617 06/17/03 07:53 PM
The purpose is to insure a resistance of <25 ohms. Some of our local jurisdictions will allow only 1 if we want to set up the megger and prove to them that it's <25 ohms. Needless to say it's cheaper, quicker and easier to just install 2
