Joined: Dec 2002
Posts: 228
OP
Member
|
Hello all, hopefully this is an easy one. I am going to be installing a small shed behind my house, no more than 10' from the rear wall. Besides trenching, which I think is overkill and can't do anyway, I was thinking of an aerial run from the attic of the house, single story, to the side of the shed, maybe a disco on the outside. There would only be one small circuit for two lights and a vent fan, so I don't think I need a sub panel or ground rods. Suggestions for wiring?
Thank you, Jim
[This message has been edited by JCooper (edited 05-13-2003).]
|
|
|
|
Joined: Nov 2002
Posts: 456
Member
|
I don't know how unorthadox this is, but run an SO extenstion cord (on a tracer, between the house and shed), plugged into the outdoor outlet on the house (with an in-use cover), with the shed wiring plugged into the cord.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
classicsat,
We can't recommend using an extension cord as a replacement for fixed wiring. See 400.8(1)
Bill
Bill
|
|
|
|
Joined: Dec 2002
Posts: 228
OP
Member
|
I had thought about just using SJOW cord to do it but I knew that was not the RIGHT way to do it, sure it would work. Do anybody know if there is such a thing as UF cable with a messenger cable to run it aerialy? Or perhaps something along the lines of service cable with ACSR but in a much smaller size, I was thinking #12 to allow for any expansion.
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
What are the requirements, if any, for lightning protection as this would be an aerial cable?
|
|
|
|
Joined: Sep 2002
Posts: 30
Member
|
I think that the only way to do this correctly is with triplex cable ext grade.. and it starts at 8 awg and is very expensive... I looked into doing a barn or two on a farm once...
[This message has been edited by RandyO (edited 05-14-2003).]
|
|
|
|
Joined: Dec 2002
Posts: 228
OP
Member
|
Is it possible to run something like seal-tight, ot other flexible duct out to it? I have some 1" tube exterior grade for running fiber in, I guess this would violate its listing. This is only a 10' run max, I would rather do this right than just run a piece of NM-B from the attic to the shed, which I would not even consider. Any suggestions would be appreciated.
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
See 1999 NEC Article 321 — Messenger Supported Wiring. {Note other articles for overhead clearance and other restrictions.}
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Why do you think trenching is overkill? You can't use portable cords or "aerial tubings". I don't think quadruplex or triplex would cost that much for such a short span. That is the right way.
[This message has been edited by Redsy (edited 05-15-2003).]
|
|
|
|
Joined: Dec 2002
Posts: 228
OP
Member
|
The reason I can't trench is that there is some HVAC equipment between the shed and house and also the fact that I rent the house, I have permission from the landlord to do all the work but I don't think she would appreciate a trench installed for a small non-permant shed.
Bjarney, I don't have a copy of the NEC handy, its at home, is there anything in there allowing me to attach UF to a messenger wire?
|
|
|
Posts: 7,382
Joined: April 2002
|
|
|
|