265
15
For new installations are you using 4 wire 4 prong plugs, or 3 wire 3 prong? I've seen dryer recepts with the neutral and ground tied together on a 3 prong plug.
Posts: 4,116 Likes: 4
Al,
New installations must be 4 wire. see 250.142(B)
We have been doing 4 wire dryer and range plugs since the '99 revision, I believe.
The owner is usually PO'ed because then we also have to install a new tail on the appliance.
FWIW GJ
I assume this includes range plugs too. Kinda strange that in the years past they were using the ground wire for a current carring conductor for the 120v clocks and timers in these appliances.
aldav53,
The equipment ground conductor has never been permitted to be used as the neutral for range and dryer receptacles. When using a 3-wire receptacle the neutral is used to ground the frame of the range or dryer.
Curt
Curt Swartz
In my area normal practice was 10/2 RX for dryers 6/2 AL SE for stoves, the bare was connected to the outlet box as ground and to center terminal of the plug.
For myself I am glad for the change to 4W plugs, if for nothing else but consistency.
Yes the 10-2 wire bare were used as grounds but we all know dryers can have 120v timers etc.
Was 10-2 w/gr ever legal for Dryers?
I thought only SE cable or 10/3 Wo/gr were legit. No books on me at the moment though. Anybody?
Bill,
I don't believe so. The bare wire in type SE cable is rated for use as a neutral conductor so it was approved for this use. That was the point I was trying to make with my previous post. I have read many comments in forums about why the 4th (neutral) wire is now required to be installed for range and dryer receptacles. A neutral wire has always been required but now a 4th wire (equipment ground) is also required.
[This message has been edited by caselec (edited 05-09-2003).]
Curt Swartz
