For new installations are you using 4 wire 4 prong plugs, or 3 wire 3 prong?
I've seen dryer recepts with the neutral and ground tied together on a 3 prong plug.
#25419 05/07/03 03:47 PM
#25420 05/07/03 07:36 PM
Al,
New installations must be 4 wire.
see 250.142(B)
#25421 05/07/03 10:42 PM
We have been doing 4 wire dryer and range plugs since the '99 revision, I believe.
The owner is usually PO'ed because then we also have to install a new tail on the appliance.
FWIW
GJ
#25422 05/08/03 11:17 AM
aldav53 Offline OP
I assume this includes range plugs too. Kinda strange that in the years past they were using the ground wire for a current carring conductor for the 120v clocks and timers in these appliances.
#25423 05/08/03 06:13 PM
aldav53,
The equipment ground conductor has never been permitted to be used as the neutral for range and dryer receptacles. When using a 3-wire receptacle the neutral is used to ground the frame of the range or dryer.
Curt
Curt Swartz
#25424 05/08/03 06:45 PM
In my area normal practice was 10/2 RX for dryers 6/2 AL SE for stoves, the bare was connected to the outlet box as ground and to center terminal of the plug.
For myself I am glad for the change to 4W plugs, if for nothing else but consistency.
#25425 05/08/03 08:11 PM
aldav53 Offline OP
Yes the 10-2 wire bare were used as grounds but we all know dryers can have 120v timers etc.
#25426 05/08/03 08:54 PM
Was 10-2 w/gr ever legal for Dryers?
I thought only SE cable or 10/3 Wo/gr were legit. No books on me at the moment though.
Anybody?
#25427 05/08/03 09:10 PM
Bill,
I don't believe so. The bare wire in type SE cable is rated for use as a neutral conductor so it was approved for this use. That was the point I was trying to make with my previous post. I have read many comments in forums about why the 4th (neutral) wire is now required to be installed for range and dryer receptacles. A neutral wire has always been required but now a 4th wire (equipment ground) is also required.
[This message has been edited by caselec (edited 05-09-2003).]
Curt Swartz