Can PVC schedule 40 marked ridgid, be run 6" underground just like steel ridgid?


The Golden Rule - "The man with the gold makes the rule"
#24741 04/22/03 06:18 AM
Joined: Feb 2003
Posts: 198
Z
Member
Table 300.5 Underground Installations,(A) Minimum Cover Requirements, should have what you need to know.


Shoot first, apologize later.....maybe
#24742 04/22/03 06:41 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
No you can not, the code refers to PVC as RNC or Rigid Nonmetallic Conduit but that does not mean the rules of RMC (Rigid Metal Coduit) apply.

As zapped said, Table 300.5 gives the info which varies depth depending on location.

Under traffic 24" (except dwellings 18")

Generally 18"

Bellow 2" cement slab 12"

Bellow 4" cement slab 4"

Under a building 0"