Got a question on Low Voltage pool lights....Do you still need the #8 insulated ground from the wet-niche to the pool junction box inside a PVC conduit?
Also check the manufactures instructions that came with it. If it says you must bond it, then you must. You would be following sec. 110-3(b) (1999 NEC)