Got a question on Low Voltage pool lights....Do you still need the #8 insulated ground from the wet-niche to the pool junction box inside a PVC conduit?

#24073 04/03/03 12:27 AM
Joined: May 2001
Posts: 552
T
Member
If the low voltage fixture is listed for use without grounding or bonding then the #8 is not required.

See 680.6(1) and 680.26(B)(2)


Donnie
#24074 04/03/03 09:41 PM
Joined: Feb 2002
Posts: 2,233
H
Member
Northern lights,

Also check the manufactures instructions that came with it. If it says you must bond it, then you must. You would be following sec. 110-3(b) (1999 NEC)

#24075 04/03/03 10:19 PM
Joined: Aug 2002
Posts: 1,081
T
Member
While on the topic of pools, here's an article from EC&M, Navigating the NEC's Rules for Bodies of Water.