#23804 03/27/03 09:58 PM
Joined: Dec 2001
Posts: 12
F
flush Offline OP
Member
hello i have quick question for ya! a rec. on a roof of a commrcial building does it need to be gfi protected? is more then 10' off the ground but the buildin steel is grounded ....in 210-63 it just says that there has to be a rec with in 25 " anyhelp wuld be great...

Joined: Jan 2002
Posts: 1,457
E
Member
FPN after 210.63 tells you to check 210.8 for gfi requirements. 210.8 (B) (2) "Rooftops"