ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 506 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Feb 2003
Posts: 169
R
Member
nesparky:
I used to think all the insulation had to be 600v also.

Russ

(1) 600 Volts, Nominal, or Less. Where circuit conductors are rated 600 volts nominal or less, both ac and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.


[This message has been edited by russ m (edited 03-28-2003).]

Joined: Feb 2002
Posts: 840
C
Member
So, by the '99 NEC this installation was not permissible, but the '02 now permits this?


Peter
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
CT,

The 1999 NEC 725-54(a)(1) Exception No. 2(b)(2)
permitted this, but the reference to 725-21 was not much help to me for understanding the intent.

The NEC 2002 725.54(D)(2)(b) says the same, but 725.52(A) Exception No. 2 tells to eliminate the Class 2 and Class 3 markings.

I, for one, question the mutilation of Factory and/or NRTL labels by anyone, let alone someone doing the field installation.

[This message has been edited by Gwz (edited 03-30-2003).]

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
For those that can, go to www.ul.com and look under ' regulators ' and then find ' Field Modification '.