I am having problems with a 2hp 460 volt vfd . It has blown the capacitors inside the drive. I megged the motor and wires and no faults there. It has happened twice. Any ideas?
|
|
|
|
Joined: Feb 2003
Posts: 138
Member
|
vfd=variable frequency drive?
If so, make sure the incoming voltage is within range and not too low, especially if the drive is reversing during it's normal run cycle.
Just a hunch......
Dave
Dave
|
|
|
|
Joined: Jan 2003
Posts: 174
Member
|
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
High temperature and overvoltage can be tough on electrolytic capacitors. Check line-side diodes to be sure one didn't fail, injecting AC into the DC bus/capacitor(s). Sometimes smaller VFDs become such a narrow-profit commodity that it’s cheaper to do a wholesale replacement. Some make good boat anchors—many do not.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
62, What sort of cabling are you using between the drive and the motor?. Is there any Mains-borne interference on the wires feeding the VFD, these units need a perfect Sine Wave input or there will be problems. Unfortunately, you will need an oscilloscope, to see what the waveshape is like, any harmonic interference on the lineside of the VFD, cause wierd currents to flow where they shouldn't. Hope this helps.
|
|
|
|
Joined: Feb 2003
Posts: 198
Member
|
62,- This could be almost anything, like maybe a scr, rectifier, diode, or trim pot. Did you take it apart to see any possible over heating on the boards? Might be a good idea to call the drive's tech dept. for some help. did you disconnect motor leads from the drive before you meggered??
Shoot first, apologize later.....maybe
|
|
|
|
Joined: Aug 2002
Posts: 112
Member
|
check the output at the d.c. bus. should be between 700 and 800 VDC, for a 460 volt drive. if its not in this range, you prolly have an SCR problem.
gramps
|
|
|
|
Joined: Sep 2002
Posts: 83
Member
|
How much torque is on your load and what is your Decel time? If your decel time is too short you will have too much regenerative current feeding back into your drive. A properly sized braking resister might help. JMHO
|
|
|
|
Joined: Aug 2002
Posts: 29
Member
|
What are VFDS? I thought it meant Vacuum Flourscent Display (VFD) Like the displays in VCRs, DVDs, Receivers etc. Those displays are also used in computers now.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Variable Frequency Drives
They control frequency and voltage supplied to standard AC motors so you can ramp them from 0 RPM to above the nameplate RPM if the motor can take it.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|