#23163 03/12/03 10:04 PM
I am having problems with a 2hp 460 volt vfd . It has blown the capacitors inside the drive. I megged the motor and wires and no faults there. It has happened twice. Any ideas?
#23164 03/12/03 11:14 PM
vfd=variable frequency drive?
If so, make sure the incoming voltage is within range and not too low, especially if the drive is reversing during it's normal run cycle.
Just a hunch......
Dave
Dave
#23165 03/12/03 11:56 PM
#23166 03/13/03 12:39 AM
High temperature and overvoltage can be tough on electrolytic capacitors. Check line-side diodes to be sure one didn't fail, injecting AC into the DC bus/capacitor(s). Sometimes smaller VFDs become such a narrow-profit commodity that it’s cheaper to do a wholesale replacement. Some make good boat anchors—many do not.
#23167 03/13/03 01:42 AM
What sort of cabling are you using between the drive and the motor?.
Is there any Mains-borne interference on the wires feeding the VFD, these units need a perfect Sine Wave input or there will be problems.
Unfortunately, you will need an oscilloscope,
to see what the waveshape is like, any harmonic interference on the lineside of the VFD, cause wierd currents to flow where they shouldn't.
Hope this helps. [Linked Image]
#23168 03/13/03 06:50 AM
Z
62,- This could be almost anything, like maybe a scr, rectifier, diode, or trim pot. Did you take it apart to see any possible over heating on the boards? Might be a good idea to call the drive's tech dept. for some help. did you disconnect motor leads from the drive before you meggered??
#23169 03/13/03 08:02 AM
check the output at the d.c. bus. should be between 700 and 800 VDC, for a 460 volt drive. if its not in this range, you prolly have an SCR problem.
gramps
#23170 03/13/03 12:01 PM
How much torque is on your load and what is your Decel time? If your decel time is too short you will have too much regenerative current feeding back into your drive. A properly sized braking resister might help.
JMHO
#23171 03/13/03 06:21 PM
F
What are VFDS? I thought it meant Vacuum Flourscent Display (VFD) Like the displays in VCRs, DVDs, Receivers etc. Those displays are also used in computers now.
#23172 03/13/03 06:27 PM
Variable Frequency Drives
They control frequency and voltage supplied to standard AC motors so you can ramp them from 0 RPM to above the nameplate RPM if the motor can take it.