Thanks for the tips guys. Those PP10's look like they would be worth the cost if you were running multiple conduits. Here's another question: I will be doing 2 other roof penetrations for an HVAC unit and a roof mounted ventilator. Do I need to install a receptacle at each location or will just 1 for everyting be okay?
Thanks again
bob

#22934 03/10/03 09:25 AM
Joined: May 2001
Posts: 552
T
Member
Bob,
The required receptacles should be within 25' of the a/c equipment based on 210.63.(guess the cmp must have felt that hvac servicemen don't carry 100'ext.cords on their trucks)

Donnie