I have a good question. If a person wants to replace their old fuse panel-with a breaker panel. Do you have to run new wire? How about the service feed? I need answers, because I'm curious. I haven't ran across an old panel in many many years, so my clarification of its looks are "none".
|
|
|
|
Joined: Dec 2001
Posts: 270
Member
|
Well, I've done a lot of west coast service changes, and a lot of the old services were only 60 Amp services. I usually installed 125 Amp breaker panels, a new riser, meter base and SE conductors, and new ground system. Usually some of the branch circuits would have to be j-boxed, in order to accomodate the new breaker panel. Old wire doesn't stretch very good. Nice one day job! Love to do service changes!
|
|
|
|
Joined: Jan 2003
Posts: 33
Member
|
I'd only consider replacing the entire service since if the fuse box needs upgrading then the rest of the system should follow suit.
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
i done alot of upgrading from old 60 amps box to modren 100 or 150 amps boxes it is very typically i do is put new meter socket new oh or ug wires setup and i make a thru inspection of exsting wires to make sure they can usebale with meet the codes and it is very common for me to rewire the kitchen and bathroom wires ( those wire are the first to go !!!!) due all the hevey load on the line some case i see old box with 30 amp with multi 14 ga wires that is very spooky that why i check it very carefull to make sure there is no burn or overload telltale signs and replace other items as need. genreally a full day some case 2 depend on how much mess it is involved
merci marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Dec 2001
Posts: 270
Member
|
Frenchelectrican, your comments about inspecting the old wiring brings to mind a common problem with service changes. After years of oversized fusing (using 30 amp fuses for #14 wire), after the service change is done the customer invariably overloads some circuits. I guess it would be good to inspect, and advise the customer about upgrading the circuitry first, so that the customer can know better about what the project will actually entail.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
We did service changes on 12, 5 story 30 unit apartment buildings right near Fenway Park. We were contracted to put in the new service and that was it, each unit had 1 #14 "riser" from the basement when we got there each units riser had a 30 amp glass Edison base fuse, when we would leave they would have a single pole 15 amp breaker. Right away these were tripping, to no surprise the floor was littered with blown 30 amp fuses.
I do not know what happened when we were gone because we got our inspection and moved on.
So for the residents it would be hair dryer or coffee maker but not both! Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Nov 2002
Posts: 558
Member
|
Marc brings up a good point.A lot of times the branch ckts are in worse shape than the service,and should be looked at closely.Russell
|
|
|
|
Joined: Feb 2002
Posts: 183
Member
|
iwire - you forgot to mention that the 14ga was cloth covered (at least where I used to live in Brighton). 5V drop when I turned on the toaster, and I kept worrying that someone would want toast and coffee at the same time one morning...
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
I wire, I have been down that road before. MANY buildings in the Boston area with that setup. One of my first jobs as a helper was in a 60+ unit building in Somerville. New service, new 60 amp panels to each apt, and new a/c and kitchen outlets all while still occupied. Quite a job. Foca Se, do you mean the feeder to the panel or the branch wiring in the house?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I did this work around 1985 I can not remember for sure but I think it was K&T
Electricmanscott, I wish we had put 60amp single phase risers in, The 800 amp 31 meter bank looked kind of strange with 30 Single pole 15s for the units and one 2 pole 100 for Public panel
Of course my 2 sets of 600kcmil feeders terminated to a #6 lead covererd underground cable assembly that Boston Edison said if it fails we will worry about it then. Bob
[This message has been edited by iwire (edited 02-22-2003).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 4,116
Joined: October 2000
|
|
|
|