4mA = 500 psi 20 mA = 1250 psi.
4-20 ma is the span 16 mA is the range
500 - 1250 psi is the span 750 is the range
7ma - 4mA = 3mA 3/16 is the % of range
3/16(750)= % of psi range = 140.625psi
Add the 140.625 to the minimumn span of 500 psi to get 640.625psi.
[(signal mA - 4) divided by 16] X (variable range) + variable minimum span
Don(resqcapt19)