#218335 03/20/17 02:49 PM
Joined: Mar 2005
Posts: 240
Member
Ok guys you are my go to answer team (much appreciated by the way). So we are doing some apartments and have come across what appears to be gray area in the code regauarding small appliance circuit. Here is a quick synopsis; we have two kitchen that supply only the kitchen, then we have a dining room that also feeds bedroom plugs only (no ceiling light switched receps)...I believe this is a violation as 210.52 lists specifically kitchen, dinining, pantry and simular, with no other outlets, however it was pointed out an exception to outlet in dining room that is a 15a and switched (I'm not sure that applys, but it adds to the confusion). Also some think because we already have the 2 small appliance you can feed whatever you want with dining circuit. Your guy's imput would help, as I said my interpretation is these rooms and simular, which definitely would not include bedroom.

Thanks,
H2O

Last edited by watersparkfalls; 03/20/17 02:52 PM.
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2005
Posts: 240
Member
two small appliance circuits feeding one kitchen...

Joined: Jul 2004
Posts: 9,919
Likes: 30
G
Member
Is this new construction or existing?


Greg Fretwell
Joined: Mar 2005
Posts: 240
Member
It is new constructin.

Joined: Jul 2004
Posts: 9,919
Likes: 30
G
Member
I hope you caught this at the FEPA/C (pre drywall) because it is a show stopper at least if the AHJ cares about the code.


Greg Fretwell
Joined: Mar 2005
Posts: 240
Member
That's what I thought too....easy fix, little money smile