I think all you "need" is two 8' ground rods on a 6 gauge GEC. You could make that better with longer rods or a ground ring. I am not sure where a plate ranks because I have never seen one or heard much about them.
I know of no rule that requires running a 250.66 GEC back to the other building. At 200', voltage drop will need to be in your calculations tho