#218256 03/01/17 06:07 AM
Joined: Jul 2007
Posts: 1,335
S
Member
I hope I make sense with this. I for looking for crimp on lug that upsizes the wire to meet the minimal terminal wire size. I don't want to pull a larger wire due to costs and needless wire fill in race way. I'm sure they are out there but I don't know their proper terminology. I'll be landing #16 gauge wire in #14 gauge terminal. Thanx up front


"Live Awesome!" - Kevin Carosa
Joined: Oct 2000
Posts: 3,682
Likes: 3
Administrator
Member

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
It may not be legal but I see guys folding the wire over so it ends up being twice the size.


Greg Fretwell
1 member likes this: tomn
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
As Greg said, folding over is seen in the field. As to it being compliant??

I understand where you are coming from with this, but I can't say I have ever seen any item to 'make it bigger'.



John
Joined: Jul 2007
Posts: 1,335
S
Member
Something like that but aren't Ferrels listed for only certain terminals? Would they work in a clam shell terminal? I may just use forks and call it good



"Live Awesome!" - Kevin Carosa
Joined: Oct 2000
Posts: 3,682
Likes: 3
Administrator
Member
Originally Posted by sparkyinak
Something like that but aren't Ferrels listed for only certain terminals? Would they work in a clam shell terminal? I may just use forks and call it good

Ahh, You didn't say what kind of terminal you were connecting to, so use a 14-16AWG Fork crimp connector and that's that?

Joined: Jul 2007
Posts: 1,335
S
Member
Just in General. I could be wrong but I think ferrels can be used on terminals listed for ferrels. I never used them nor I'm not a fan of them. Seems like a lot of work when simple craftmenship gets the job done right without the added costs of ferrels


"Live Awesome!" - Kevin Carosa