1 members (ale348),
302
14
Anonymous
Unregistered
Can you place romex in EMT? Where in the code does it say you can or cant? I have asked this question to 3 electricians and got 3 different answers. Its a 40' run of 1/2"emt with 10/3 romex going into it. Thanks for any help.
WildTurkey101; check out page 70-617 of the 02' , notes to tables #9 btw~ welcome to ECN
99NEC Ch.9 Notes to Tables “A multiconductor cable of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.”
Not sure if this would be the case for “Over 2 Wires: 40%” or “1 Wire: 53%” fill. 10/3 NM-B will probably need larger than ½-inch tubing.
WildTurkey101...( I have asked this question to 3 electricians and got 3 different answers.)...so what was their answers. is the 10/3 cable being installed in the conduit for protection against physical damage.? sparky ....what page.
wildturkey :
for 10/3 romax cables(wires) you have to run it in 3/4 emt conduct. btw 1/2 inch conduct wont fit with 10/3 belive me it is a pain in the butt with that but i did check on nec 99 version it say same way check the area fill for conduct
merci marc
Anonymous
Unregistered
Lighthouse, the answers were "yes you can", "no you cant", and "what the heck are you talking about". The 10/3 is running down the side of a house and I was going to place it in some EMT. I just wanted to make sure I wasnt breaking any code rules. Thanks for all the quick replys.
Posts: 466 Likes: 1
Is this running down the inside or outside of the house?
Anonymous
Unregistered
Jim, it is running along the outside of a house.
just to make your morning i'll ask if if needs to be grounded....
