This rule says that electrical equipment rooms must have sprinkler drip shields on electrical equipment.

Does not say other rooms. Am I to assume that having a bit of water spray into panels is acceptable in other areas?

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Appendix B explains that the problem is ventilated enclosures.

Joined: Mar 2006
Posts: 82
B
bigpapa Offline OP
Member
I spoke to the inspector having jurisdiction and he said that drip protection definitely required for electrical rooms as stated in the rules, but will also enforce in other areas if its possible for water to pool on top of the panel board.

In this case side entry allowed unless using connectors capable of greatly restricting the amount of water allowed in. Oddly a dry type EMT connector would be accepted for top entry, a flex connector not.

Gray area. Best to check first.

Joined: May 2001
Posts: 378
F
Member
I've been there.I would call him and see.He had no problem showing up and telling me what he wanted.The existing installations were allowed to exist as is.