Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
I can't find the rule about the angle at which a conduit can enter a box through a KO. Is there one? It might have something to do with the need for a ground bushing because too much angle lifts one side of the lock nut (and connector) off the surface of the box.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Off the top of my head, I can't put a specific NEC Article on it, except 110.12 regarding mechanical execution of work.

However, this Article is basically unenforceable as it is 'subjective' as to "neat and workmanlike manner".

Your comment regarding the connector/locknut not being flush with the KO goes back to NEC Art 250 and a 'stretch' would be NEC Article 110.3 (B): re. mfg install instructions.




Last edited by HotLine1; 06/04/16 12:59 PM. Reason: add comment

John
Joined: May 2005
Posts: 984
Likes: 1
G
Member
I'm not aware of anything beyond 'neat and workmanlike manner".


Ghost307
Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
I thought it was a Canadian code or in a provincial supplement.

Joined: Jul 2008
Posts: 98
Likes: 1
B
Member
Originally Posted by twh
I can't find the rule about the angle at which a conduit can enter a box through a KO. Is there one? It might have something to do with the need for a ground bushing because too much angle lifts one side of the lock nut (and connector) off the surface of the box.

12-1008 requires at least 3 complete threads.

I would think that you're limited to going straight in.
Any bends would be made outside of the box.

Joined: May 2003
Posts: 1,158
Member
I would really want to use a reducing washers but that really wont give you enough threads,#2/3 acwu i need to use a 3/4 throat wet connector into a meter base and I seem to feel more comfortable to use the reducing washers on the larger Ko;s on MB