#217136 - 05/13/16 04:44 PM Working space in front of elevated busduct system
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Existing warehouse. 2000A service feeding busduct hung off of outside wall. Busduct is 12 feet above floor. All connections from disconnects go up. Owner wants to put workbenches and tool storage cabinets no taller than six feet, below bus, along the wall.

Electrician says no, need to maintain working clearance. I thought the only requirements were 36 inches in front of, six feet or hard ceiling above, and four feet below bottom of disconnect.

Am I completely off base?

Thanks
Top
Work Gear for Electricians and the Trades
#217148 - 05/16/16 05:05 AM Re: Working space in front of elevated busduct system [Re: LarryC]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
I think the Electrician is correct.
How would you access the bus without moving the cabinets?
_________________________
Ghost307
Top
#217151 - 05/16/16 09:57 AM Re: Working space in front of elevated busduct system [Re: LarryC]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
What is in the bus duct? Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?

Can they simply put a catwalk over the cabinets? They are 12' AFF. What is the access now?
_________________________
Greg Fretwell
Top
#217152 - 05/16/16 02:58 PM Re: Working space in front of elevated busduct system [Re: gfretwell]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Quote:
Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?


That was my point. If you have to move or add a disconnect, then move the benches or cabinets at that time. Otherwise the only expected operation while energized would be operating the disconnect via an insulated pole.

Fuse replacement would be done after operating the disconnect and access to the disconnect is easily arranged by step ladder or manlift.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals