#216990 - 03/25/16 11:14 PM 3 phase star heater confusion
johno12345 Offline
Member
Registered: 09/13/05
Posts: 96
Loc: United Kingdom
Hello, its been a while!

I have a heat pump with a 6kW 3ph star electric accessory heater

I thought it wasn't working properly, and to cut a long story short, I clamped the terminals, and got a load reading on only one phase.

I have drawn it out, to try and make sense of it. I have a theory as to why its working as it is, but ill get to that in a later post.

_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough
Top
Work Gear for Electricians and the Trades
#216991 - 03/26/16 03:58 AM Re: 3 phase star heater confusion [Re: johno12345]
geoff in UK Offline
Member
Registered: 12/30/02
Posts: 179
Loc: UK
The only way I can see those readings occurring is if heater 1 is open circuit but with an earth fault at the right hand end. Heater 3 must also be o/c or have no supply.
Top
#216992 - 03/26/16 09:27 AM Re: 3 phase star heater confusion [Re: johno12345]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
The only way that those amperage readings make any sense to me is if HEAT3 (or LS3) is open and HEAT1 is shorted to ground on the line side.
That would leave HEAT2 as the only working element; but it's using the metal housing as the return path instead of being routed to L1 via the HEAT1 coil.
_________________________
Ghost307
Top
#216993 - 03/26/16 09:38 AM Re: 3 phase star heater confusion [Re: johno12345]
johno12345 Offline
Member
Registered: 09/13/05
Posts: 96
Loc: United Kingdom
that's what I think is happening too. (its what I alluded to in the first post)

I don't think it would operate any cpd either. I didn't get a shock touching the case of the unit. It's still a safety issue though.

woulnt this happen if any element went down to ground though, and not operate the cpd? The only way to protect it would be to install a RCBO/RCD (GFI)
_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough
Top
#216994 - 03/26/16 02:17 PM Re: 3 phase star heater confusion [Re: johno12345]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
The breaker won't trip until it sees more current than it's rated at. Depending on where the short is the current value on any given phase may not get high enough.

A GFI might do the trick; but only if the return current isn't somehow coming back on one of the phase legs.
If this was something expensive I'd suggest a protective relay that would operate if the current on the 3 legs differ from one another.
_________________________
Ghost307
Top
#216995 - 03/26/16 02:34 PM Re: 3 phase star heater confusion [Re: johno12345]
johno12345 Offline
Member
Registered: 09/13/05
Posts: 96
Loc: United Kingdom
its not something expensive, its just a heat pump with the accessory heater.

I can understand how it's all working as it is, it just sounds a bit alarming

it must be a fairly common failure mode for these things
_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough
Top
#216996 - 03/26/16 06:35 PM Re: 3 phase star heater confusion [Re: johno12345]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
My guess is it started with the ground fault on heater 1, that one blew along with #3 because now they are seeing 120v instead of 104v and #2 is living on borrowed time.

What is the name plate power consumption? 3KW?

_________________________
Greg Fretwell
Top
#216997 - 03/26/16 07:24 PM Re: 3 phase star heater confusion [Re: johno12345]
johno12345 Offline
Member
Registered: 09/13/05
Posts: 96
Loc: United Kingdom
6.9kW, and its 400v between phases, so if the earth fault is where you have drawn it, heater 2 is seeing 230v, rather than 400
_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough
Top
#216998 - 03/26/16 07:56 PM Re: 3 phase star heater confusion [Re: johno12345]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The heaters are in series so the phase to phase voltage is split between them. Unfortunately I am still having the numbers to come out right with this calculator.
https://www.watlow.com/reference/tools/3phase.cfm


_________________________
Greg Fretwell
Top
#216999 - 03/27/16 09:25 AM Re: 3 phase star heater confusion [Re: gfretwell]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Greg,

Since there is no contactor for the third phase, they may be using a corner grounded delta. In that case, the heating element will see the full 400 V across it and the current will be approximately double of the calculated. That comes a bit closer to the measured values.
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals