#216753 02/11/16 08:13 PM
Joined: Oct 2002
Posts: 830
S
Member
Could someone refresh my memory on the use of AFCIs in the kitchen? GFCIs are still required around the counter, but code says that kitchens require AFCI's too. How's this accomplished? A combination device?
Thanks..

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

sparkync #216755 02/11/16 09:40 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Personally, I'd either use an AFCI breaker with a GFCI device downstream, or an AFCI device feeding a GFCI device.

sparkync #216759 02/12/16 02:34 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Cuttler Hammer does sell a GFCI/AFCI combo breaker but I agree with Reno. Trouble shooting is easier if you have a GFCI device at the counter top.
I really had to look this one up because we are still on the 11 here and that is a 14 requirement. I was thinking the kitchen was exempt. Silly me.


Greg Fretwell
sparkync #216764 02/14/16 01:54 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Just something to make you guys laugh....

Final on a resi addition, panel had 3-GFI CBs, no AFCI CBs.
H/O said.."I know he put them in, I paid extra".

Went to kitchen.....wow, the elusive AFCI devices!! And, they were not on the GFI CBs!!

BTW, this job was not DIY, it has a EC!!




John
HotLine1 #216776 02/17/16 01:52 AM
Joined: Oct 2000
Posts: 5,392
S
Member
Rumour is 210.12's requirements will be all 120V circuitry in the '17 , and 210.8's 'readily accessible GFCI' is making DP (dual purpose) breakers much more appealing, considering the 'gfci under the sink for the pig/dish' debate.....

Myself, a DP 50A spa disco setup ahead of an MLO panel kitchen subpanel may be a consideration .....

~S~