#216438 - 12/18/15 05:30 AM Nail salon ventilation
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
I'm checking a job(nail salon) that requires ventilation. The safety inspector left a paper with the owner that says that "systems shall be capable of exhausting a minimum of
50 cfms per station. Has anyone run across one of these? The business I am looking at has around 6 chairs for customers. I'm guessing that if I put a 300 cfm fan in the middle that should do it. I left a message with one of the inspectors, but they have not returned my call. Any ideas?
Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#216443 - 12/18/15 11:35 AM Re: Nail salon ventilation [Re: sparkync]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I'd ask the inspector! Better yet, find the exact code he's using, and see what the code says.

Evacuation of solvent fumes is a BIG inspection issue for nail salons. Be sure to take into account the cfm lost in every bend of the pipe. Be sure to provide for make-up air.

As I recall it, the ventilation needs to be present at each station; general room ventilation won't satisfy the requirement. They might let you put the fans on timers. I quoted one such job, only to have the owner choose to play inspection / responsibility games instead. Oh well. frown
Top
#216472 - 12/20/15 10:35 AM Re: Nail salon ventilation [Re: sparkync]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
sparkync:

A ventilation system for nail salons here is required to have a plan prepared by an Architect or Engineer.

Usual is a 'common' exh fan, trunk duct. and a 'drop' at each workstation. Some have a 'on/off' switch at each station, some are a 'one switch' control at reception.

IMHO, the mechanical install of this type of system is best left to a mechanical contractor (HVAC).


_________________________
John
Top
#216480 - 12/20/15 10:14 PM Re: Nail salon ventilation [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I agree with John. Just ask the HVAC guy where he needs the power and be done with it. Around here, he needs to run the duct anyway if it is more than a short 4" flex to the nearest "out". (no venting in the attic or anything)
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals