#216435 - 12/16/15 03:42 PM Internet bonding to sub-panel
flitch Offline
New Member
Registered: 12/15/15
Posts: 2
Loc: Western NY
Homeowner has Time Warner internet telephone cable direct to sub-building. Sub-building serviced by 4 wire 150A sub-panel fed from main 200A panel 100 feet away with ground rods located (1) at the main panel and (2) at the sub-panel, both bonded back to their respective ground bus. The sub-building has gas heat so the CSST pipe is bonded to the ground rod (for convenience) vs being bonded inside the panel. Can the internet cable be bonded to the same rod which would then make a loop of the internet cable directly from the sub-panel (via the cable) to the pole? Isnít this likely to be current surge problem for the internet cable fed devices.
Top
2017 / 2014 NEC & Related Books and Study Guides
#216436 - 12/16/15 05:45 PM Re: Internet bonding to sub-panel [Re: flitch]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
More grounding is better in a surge situation. You want a single point ground on your side of the building entrance, preferably right where the main bonding jumper connects to the grounding electrode conductor (same bus bar). That should be where the inter system grounding bus lands. Any "loop" created on the line side is your phone company's problem and they are well prepared to deal with it. They reground their stuff at every drop.
_________________________
Greg Fretwell
Top
#216442 - 12/18/15 11:31 AM Re: Internet bonding to sub-panel [Re: flitch]
flitch Offline
New Member
Registered: 12/15/15
Posts: 2
Loc: Western NY
Thanks, Greg.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals