#216141 10/16/15 03:50 AM
JUJU Offline OP
New Member
I have seen an excel sheet in calculator to calculate the size of transformer.
There are option to put the vales of Kw,PF,Qty and Equipment D.F.
I could not understand what is D.F.
What is the equation to calculate the D.F and equation to calculate the total load D.F?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
D.F. is probably the Demand Factor.
What percentage of the transformer rating is being used.
Ghost307
New Member
DF= Demand Factor...a ratio portion of the total demand load of a system (or system part) expressed as a percentage calculated for usage allowed. [Art.220]
New Member
Note that including the overall Demand Load depends on using a standard or optional method load calculation as permitted in Art.220 for determining the transformer rated capacity size needed.