Topic Options
Rate This Topic
#216019 - 09/07/15 05:47 PM 2500 amp service
Merlin Offline
Loc: NW Indiana
Looking for some suggestions.....I am quoting a job to install a 2500 amp, 480/277V service. This will be feed from a pad mount transformer about 30 feet into a building. Obviously it will be parallel conductor fed. What combination would you all use? 750kcmil, 1000kcmil,.....any thoughts?
Top
#216020 - 09/07/15 05:56 PM Re: 2500 amp service [Re: Merlin]
twh Offline
Loc: Regina, Sask.
Aluminum. Then, all sizes are easy.
Top
#216021 - 09/07/15 06:35 PM Re: 2500 amp service [Re: Merlin]
HotLine1 Offline
Loc: Brick, NJ USA
Merlin:
Common is 6 sets of 600 KCMil Cu THHN/THWN in 4" PVC
You have to check the secondary 'window' of the pad mount xfr., as that limits the quantity of conduits you can install.
_________________________
Top
#216042 - 09/15/15 09:19 PM Re: 2500 amp service [Re: HotLine1]
Merlin Offline
Loc: NW Indiana
Correct me if I'm wrong, but 6-600's would be
6 x 475 = 2850.
Derated for 4 conductors in conduit(480/277) at 80%
2850 x .8 = 2280.
Wouldn't it be 6x750kcmil?
6 x 535 = 3210
3210 x .8 = 2568
Top
#216045 - 09/16/15 08:35 AM Re: 2500 amp service [Re: Merlin]
HotLine1 Offline
Loc: Brick, NJ USA
Merlin:
I stand corrected....I did not 'see' 2500 amps.
Top
#216073 - 09/21/15 11:10 PM Re: 2500 amp service [Re: Merlin]
Scott35 Offline
Loc: Anaheim, CA. USA
If this Installation is for Service Feeders (from a Poco Transformer to Service Equipment), you need to verify the requirements with the Service Planner before bidding this Project (or before commencing the actual work!)
If the Installation is on the LOAD side of the Service Disconnect, then (6) 4" Ducts with 4-750MCM CU. per duct is sufficient... if NO Equipment Grounding Conductors are installed!
If an EGC is to be installed, that will be a minimum of (1) 350MCM CU. per duct, so now the Ducts would be 5" (???)
dunno
--Scott (EE)
Top
SE cable question
2017 NEC and Related
2017 NEC
Now Available!
Shout Box
Who's Online
0 registered (), 95 Guests and 10 Spiders online.
SE cable question
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN
ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals