#215719 - 07/07/15 07:37 AM 680.22(B)(1) and post lamps
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
For the purposes of 680.22(B)(1) is the post considered as part of the luminaire? (2011 NEC)


Edited by BigB (07/07/15 07:37 AM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#215721 - 07/07/15 07:59 AM Re: 680.22(B)(1) and post lamps [Re: BigB]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
IMHO, the 'post' is the support for the luminaire. The post height must place the luminaire at 12' above water.

The few that I have come upon used fiberglass/composite poles at 14', and on GFI circuit.

You should check with your local AHJ for his opinion.
_________________________
John
Top
#215723 - 07/07/15 10:13 AM Re: 680.22(B)(1) and post lamps [Re: BigB]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I agree with John on this. The post is just a support for the luminaire. If it is metal it needs to be part of the bonding grid too.
_________________________
Greg Fretwell
Top
#215726 - 07/07/15 11:28 AM Re: 680.22(B)(1) and post lamps [Re: BigB]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Thanks Greg, I omitted the bonding on metallic posts.

Squeezing in posts between hectic times in the office.
_________________________
John
Top
#215742 - 07/11/15 11:06 PM Re: 680.22(B)(1) and post lamps [Re: BigB]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
We ended up moving one the lights. The original plans showed that we would have had over 5 feet but when the pool got dug and laid out somehow there was a foot missing, not our fault. They are post lamps mounted on top of a retaining wall so moving one was a lot of fun carving up the concrete blocks.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals