#214818 - 01/28/15 03:33 PM Minimum height for disconnect on mobile home
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
Somewhere is the previous codes I remember the minimum height of a disconnect on a mobile home was 2 ft. I have a potential job that the meter and panel is burnt up, and needs replacing. The height now is only 18 inches, and it will have to be dropped about 2 or 3 inches so that the wires will reach the new "feed thru" panel. I can't seem to find it in the 2011 code book I'm looking in. Can anyone help me find this. I talked with the local inspector and he didn't seem to know and said I might have to run new wires to the inside panel to get the panel high enough. Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#214820 - 01/28/15 05:04 PM Re: Minimum height for disconnect on mobile home [Re: sparkync]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
This is the first I have heard of a 'minimum' level. If there were one, I expect it would be found in the standards of the local PoCo.

PoCo standards are not binding when the park does its' own billing.

"Standard" Service pedestals seem to place the meter at about the 4-ft. level. Such pedestals have, as part of their base, an accessible trough that extends into the ground. I would expect that you can splice the wires in that trough, to reach where you must.

How to splice? My first choice would be crimps, wrapped in tape and covered with Scotchkote. NSI's Polaris connectors would be my next choice, similarly sealed with Scotchkote.
Top
#214823 - 01/28/15 05:54 PM Re: Minimum height for disconnect on mobile home [Re: sparkync]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
It's in 550.32.
_________________________
Ghost307
Top
#214824 - 01/28/15 08:50 PM Re: Minimum height for disconnect on mobile home [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Ghost is right on

Quote:
(F) Mounting Height. Outdoor mobile home disconnecting means shall be installed so the bottom of the enclosure containing the disconnecting means is not less than 600 mm (2 ft) above finished grade or working platform. The disconnecting means shall be installed so that the center of the grip of the operating handle, when in the highest position, is not more than 2.0 m (6 ft 7 in.) above the finished grade or working platform.
_________________________
Greg Fretwell
Top
#214826 - 01/28/15 09:26 PM Re: Minimum height for disconnect on mobile home [Re: sparkync]
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
Thanks a lot. I knew it used to be in there. I just couldn't find it.
Top
#214828 - 01/28/15 09:57 PM Re: Minimum height for disconnect on mobile home [Re: sparkync]
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
If I put a pvc junction box under the panel to make splices, and have 2" pvc coming in one side from the bottom and 2"pvc going out the other side up to the panel, will the size of the junction box have to be at least 12" since 314.28 (2) says that it must be 6 times the largest raceway entering the box? My other question would be how deep would it have to be? 12x12x12? or could it be 12x12x8 ?? sort of confused on the depth.
Top
#214830 - 01/29/15 01:19 AM Re: Minimum height for disconnect on mobile home [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I don't think the depth is addressed directly but you still need enough volume for the fill. This is mainly just addressing the bending space laterally
_________________________
Greg Fretwell
Top
#214832 - 01/29/15 07:01 AM Re: Minimum height for disconnect on mobile home [Re: sparkync]
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
Thanks Greg. I couldn't see that it was either.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals