ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#214524 12/18/14 09:35 AM
Joined: Oct 2014
Posts: 5
P
PN1 Offline OP
New Member
Greetings fellow electricians and engineers. I have a question regarding EMS System filters( Adresses linear Vs Non linear loads). I have a project that requires an EMI fiter. The Characteristics are.

Max Applied Volts 230VAC
Operating frequency 50Hz
Maximum current Amperes 125Amps
Number of Phases 3

? How do I calculate the maximum value of the currents leakage ?
Regarding attenuation, How does one calculate the required attenuation ?.
Your opinions are much appreciated, Thank you.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

PN1 #214543 12/20/14 01:34 AM
Joined: Jul 2004
Posts: 787
L
Member
Regarding attenuation, How does one calculate the required attenuation ?.

What frequency range are you trying to attenuate?

Is the product a variable frequency drive? They make line side inductors to smooth out the current spikes and reduce the noise getting into the power system from the VFD.

PN1 #214572 12/22/14 10:30 AM
Joined: Oct 2014
Posts: 5
P
PN1 Offline OP
New Member
The frequency is 50Hz. This is not a VFD, There are no potentiometers analog or PLC driven functions. Its a filter for RF emmanations. Its function adresses linear Vs. Non linear loads. Its basically a noise filter and transformer built into one unit.

PN1 #214577 12/22/14 10:09 PM
Joined: Jul 2004
Posts: 787
L
Member
A line filter and a transformer are two different things. I suspect you are looking for a three phase common mode choke.

CorCom is a common manufacturer here in North America.

Go to corcom.com and look thru their catalog. They have three phase line filters that may be just what you are looking for.

Joined: Jul 2004
Posts: 787
L
Member
More thoughts.

When filtering for RF emissions, make sure the noisy side of the power mains are separated from the shielded side of the power mains. Shielding may include a separate shielded compartment around the line filter and no mixing of the shielded side wires with the noisy side wires to prevent the RF interference from coupling onto the clean side.

To reduce radiated emissions from the system, tie all shielded cable shields to a 360 degree shielding bar before entering the noisy enclosure. Make sure that the longest dimension of the openings in the enclosure are less than 1/10(?) of a wavelength of the highest frequency of concern. Usually that means shielded fan grills and overhanging sheet metal so there is not a line of sight opening between the interior and the exterior of the noisy box.

Here is a good primer on shielding: EMI shielding primer

Good Luck

Larry

PN1 #214581 12/23/14 03:43 AM
Joined: Oct 2014
Posts: 5
P
PN1 Offline OP
New Member
Thanks Larry, Insight is much appreciated.

PN1 #214592 12/23/14 11:17 PM
Joined: Jul 2004
Posts: 787
L
Member
Your welcome.

Good luck with the project.