#214531 - 12/18/14 07:28 PM derating rooftop conductors
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?
Top
2017 / 2014 NEC & Related Books and Study Guides
#214533 - 12/19/14 12:54 AM Re: derating rooftop conductors [Re: BigB]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.